Ground System Testing Requirements
mdgardner
Roswell, GA
Electrical Engineer
I have a client (manufacturing facility) looking for how often they should be testing their grounding system and what kind of testing they should be doing? I've found a lot of information on testing ground resistance. Is this all that all the testing that is required? what about maintenance of connections, etc? How often should these be checked?
Thanks!
Why would you test something like that at all? Do a visual inspection annually. That is about all that is needed unless you have something very special like a cell tower.
If the customer wants to spend money for no good reason there are all kinds of tests that can be done.
In accordance with NETA there's a test for it, Acceptance and Maintenance tests. In the 2015 version of the Maintenance Testing Specification it's section 7.13 Grounding Systems. There are point to point tests, along with a Fall of Potential (FOP) test on the assembled system. The minimum acceptable limits for the FOP test for industrial/commercial systems is 5 ohms and it's less than 1 ohm for generating/transmission systems.
I used to require it on our biannual Power System PMs when I worked in industry where all of the electrical systems were maintained in accordance with industry standard. Scott Paper and P&G both support maintenance for electrical systems. And it's the only way that arc flash labels are applicable, if the electrical equipment maintenance is to industry standard. So corporate-conscious employers keep their electrical systems maintained.
Is this correct? I understand the need for maintenance of OCPDs, I guess I would not have considered ground system testing a requirement for validating results of an arc flash study - don't all the arc-flash calculations assume L-L faults?
I'm referring to ocpd testing to put the system into the "Normal" category in 70E, so I don't think ground-testing would negate that classification. But ground testing would be part of a comprehensive Power System PM.
One thing often neglected IF you have an isolated-ground setup is to make sure that it's still isolated. Usually this meant that during a full downtime, the factory electricians would de-energize a branch circuit, lift the IG conductor, and test continuity to the GES; if there was, they'd start at the far end and work back looking for something that would cause the fault. Called it "ground-hogging" :LOL:.