Re: Ground tails through slab
Bennie, I will try to explain. When metallic enclosure are made of magnetic material such as steel, the "choke effect" is much greater than in metallic non-magnetic materials, such as alluminum. The reason for this is that the magnetic field associated with the wire is "amplified" when it is brought within the vicinity of the magnetic material(the amount of magnetic flux availible to induce current in the iron increases). This "amplification" effect occurs becaause of the "permability" of magnetic materials is greater than 1. "Permability" is, simply, a number that measures the ability of the material to "amplify" a magnetic field in the presence of current. The greater the permability, the greater the amplification effect.
What does it all mean? It means if you run a GEC in steel conduit without bonding, you would incur a greater voltage drop during a surge event, as opposed if you did bond it.
Here are some interesting mathmatical models of voltage drop on conductors in free air and then conduit based on a 3000 amp in 8 microseconds strike which is a modest number.
1 inch free air = .75 volts 1 inch in conduit = 394 volts.
1 foot in free air = 75 volts, 1 foot in conduit = 4875 volts.
10 foot in free air = 1200 volts, 10 foot in conduit = 48,000 volts.
100 foot in free air = 17,250 volts, 100 foot in conduit = 486,000 volts.
If the models are correct it is clear flashover can and will occur. Hope that helps. Dereck