Ground Test

Status
Not open for further replies.

jamal

Member
What is the best way to determine the effectiveness of the individual Ground Rod and how many Ohm thank you
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Ground Test

I think the best way is to disregard the ohms of the first rod, and simply install a second. With two rods, you don't need to measure. But I'll have to let someone else answer your question.
 

karl riley

Senior Member
Re: Ground Test

And also ask yourself, effective for what function? The average ground rod impedance is a little over 100 ohms in 5 midwestern states. Is the 100 ohm rod not effective? You have to know what it's for.

Karl
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Ground Test

There is really no way to determine the effectiveness of a ground rod. It's intended function (to help disperse lightning and surges) can't be accurately measured.

Roger

[ August 22, 2003, 12:36 PM: Message edited by: roger ]
 

brian john

Senior Member
Location
Leesburg, VA
Re: Ground Test

The best approach is to perform a 4 point earth ground resistance test PRIOR to installing a ground electrode system.

This test will assist in determining the design of the grounding electrode system (assuming you have a spec or standard to meet).

After the system is installed a three point test is utilized to determine the effective resistance of the ground electrode. Of course this value will change due to weather condition, after lightning strikes ect..........

There are numerous sites with information www.lyncole.com for starters
 