Ground Testing for Large Buildings

Status
Not open for further replies.

Sunny_92

Member
Location
York, PA
Occupation
Electrical Engineer
I'm looking for a little input from someone who has experience performing grounding system testing.


If you were asked to perform standard NETA maintenance testing on the grounding system at a large building on a relatively tight site, such as the one pictured here, how would you go about it? Let's assume there is a ground ring around the entire building.


To measure the electrode-to-ground resistance, it would seem problematic to use the standard fall-of-potential method because of the large test probe spacing required. Assuming the ground ring runs around the entire building, the max dimension of the electrode system would be about 750' which would require the current probe to be placed well beyond 1000' using the standard FOP method. Even using the Slope Method (Intersecting Curves Method) would require the current probe to be placed over 1000' away which is infeasible.


The only good alternative I can think of is using a clamp on ground tester at the service point. The particular site used as an example here has an underground medium-voltage feed from the utility that serves the customer's MV switchgear lineup. I'm thinking we can make appropriate use of a clamp on meter if we measure at the point that the concentric neutrals combine and connect to the ground bar. Would you consider this to be an acceptable way of measuring the electrode system resistance?

Any thoughts?

Site.jpg
 
it seems to me if you are required to perform the testing IAW a specific standard your choices are limited to what the standard allows you to do.
 
I know nothing about standard NETA maintenance testing so what is the purpose of this testing? IMO the more important test would be the main bonding jumper.
 
I would identify all grounding points in the structure and micro-ohm test each point. In addition I would check the connection for its mechanical strength in the case of thermo weld.


Sent from my iPad using Tapatalk
 
I'm rusty on these, been a while but as I recall the slope method is what you would use for this. a 1,000ft C probe lead is fairly common with most test sets.
 