Zog,
Thanks for the info. Now, how can I prove that the simple ground test performed by the testing company does not prove that the grounding and bonding of the building is in compliance with the NEC? This guy is doing everything he can to avoid installing a GES per code because he neglected to be on the job when the building was coming out of the ground. For instance, there is no connection to a concrete encased electrode which was available (of course not now because the floor is poured), isolated structural steel for bridge cranes that are not connected to other building steel, a seperate ground rod driven at the front of the building but not connected to the main grounding system, the office structural steel is isolated from the plant steel and not bonded to anything, there is a sprinkler piping system not bonded to anything, a steel gas piping system not bonded to anything, a 75 KVA transformer that is has no bond on the XO tap, embedded rails (like train tracks) in the floor that machinery travels on not bonded to anything. I could go on and on. Of course this is the work of a guy that told us that the main bonding jumper in the switchgear was of no consequence if he had the ground bus connected to a ground rod. I am at my wits end argueing this. The local building official (which is not an electrical inspector) gave them the OK based on the fact the testing firm issued a letter stating that grounding meets code.