I have a situation that I have come across at with a commercial customer that we do electrical work for. It deals with the Ground to Neutral voltage. This is the situation I have.
3rd floor of a production facility in a office area. office personel complain of a slow computer system, they called the IT department and the IT specialist comes down and the first thing he does is plug in a power diagnostic tester that basically has about 15 light on it and it test for high and low voltage, properly grounded, properly wired and then the one that always causes us problems is the ground to neutral voltage. His test instrument has 3 lights for this catagory <.5v gives OK light, <1v gives yellow warning and >1v red danger light. We always get called in when it is a yellow or red light situtation basically ground to neutral voltage >.5v
When I first went into the room I had 2.3 volts from ground to neutral. As the person was clearing out of the office for me to work I retested voltage after she left and I had .3 volts ground to neutral. After some searching and testing I discovered that the coffee pot would cause my G-N voltage to go from .3 to 1.3volts. She also had a floor radiant heater when turned on caused a G-N voltage of 2.5 volts.
We have been running individual circuits from each recepticle back to the power panel to eliminate this problem. Now we are running into the problem of them plugging the coffee pot into the same yoke as the computer which caused the same problem.
Am I missing something or is this typcial for neutral impedence on the neutral. Is this common and it is only noticed when dealing with electronic equipment?
Jim Gavin
3rd floor of a production facility in a office area. office personel complain of a slow computer system, they called the IT department and the IT specialist comes down and the first thing he does is plug in a power diagnostic tester that basically has about 15 light on it and it test for high and low voltage, properly grounded, properly wired and then the one that always causes us problems is the ground to neutral voltage. His test instrument has 3 lights for this catagory <.5v gives OK light, <1v gives yellow warning and >1v red danger light. We always get called in when it is a yellow or red light situtation basically ground to neutral voltage >.5v
When I first went into the room I had 2.3 volts from ground to neutral. As the person was clearing out of the office for me to work I retested voltage after she left and I had .3 volts ground to neutral. After some searching and testing I discovered that the coffee pot would cause my G-N voltage to go from .3 to 1.3volts. She also had a floor radiant heater when turned on caused a G-N voltage of 2.5 volts.
We have been running individual circuits from each recepticle back to the power panel to eliminate this problem. Now we are running into the problem of them plugging the coffee pot into the same yoke as the computer which caused the same problem.
Am I missing something or is this typcial for neutral impedence on the neutral. Is this common and it is only noticed when dealing with electronic equipment?