Ground up on outlet with metal plate

Status
Not open for further replies.

Mustang125

Member
Location
New Hampshire
Occupation
Master Electrician, Project Manager and Estimator
Hello
i can’t seem to find it in the code but it has been common practice at my company to put the ground up when using a metal plate. A lot of guys think it’s a code, is it? I guess the theory behind it makes sense, if the plate was to shake loose (very rare, but possible) it would fall and short out.
Thank you
 
Hello
i can’t seem to find it in the code but it has been common practice at my company to put the ground up when using a metal plate. A lot of guys think it’s a code, is it? I guess the theory behind it makes sense, if the plate was to shake loose (very rare, but possible) it would fall and short out.
Thank you

The NEC does not care. Both are fine and legal. Myth that it is or was ever code mandated that it be one orientation or the other.
 
It's in the Urban Legend Electrical Code. 3125.934(A)(17)(c)(614.2). Right after 'No Wire Nuts Allowed in Panels'.

Some jobs will have the requirement as a specification, but that's strictly a design choice.
 