Re: ground vs isolated ground
CaptainKevin, you are on a tough road. The first step is to trace out all the IG's and EGC's back to the power source. You need to be sure the IG's are truly isolated as they pass through any panel and junction boxes.
The IG's, EGC's, and grounded circuit conductor (neutral) should be bonded together at the service entrance or isolation transformer if used. Find this bond point and measure your voltages there. They should all be zero at that point with respect to each other.
Next you need to make sure you have a GEC connected to the same point as mentioned above. Again this will be at the service entrance or isolation transformer is used.
You may find that the IG originates downstream from the N-G bond point say at a sub-panel. This does comply with code, but not a proper design.
If everything checks OK then I suspect you have a RFI problem. If that is the case an IG circuit will be of no use, and will only compound the problem, since it acts as an antenna. An SG circuit that is multi-grounded would lower the voltages, but not enough. IG's, EGC, and GEC are only for safety, and are not suitable for HF work.
You may have to consider using other techniques such as balanced power, isolation transformers, balanced or optical signal transmission rather than a ground referenced medium to eliminate the problem. It could be as simple as installing a isolation transformer where the A/V equipment is located then run dedicated SG circuits to power all the A/V equipment.
Let me know more details, and I will try to help.
Good Luck
Dereck