Is there an NEC requirement that a service ground needs to be run in the same conduit as the current carrying conductors or can it be run in a separate conduit?
You are welcome. Sorry to sound a little harsh on correct terms, but the NEC correct terms are critical to avoid confusion.@texie; that's what I thought. I'm curious what the code reference is, I'm not finding it specifically in 250...
300.3(B) got it! Thank you.
No worries. I greatly appreciate the info.You are welcome. Sorry to sound a little harsh on correct terms, but the NEC correct terms are critical to avoid confusion.