Can someone show where it says in the NEC that you can use a #6 bare copper ground wire to both ground rods. There is a argument that you must use a #4 bare copper minimum to both ground rods for a 200 amp service.
Brad Baxter said:Can someone show where it says in the NEC that you can use a #6 bare copper ground wire to both ground rods. There is a argument that you must use a #4 bare copper minimum to both ground rods for a 200 amp service.
wbalsam1 said:C3PO is correct when he refers to 250.66(A). However, in my jurisdiction and that of my fellow employees, NYSEG, National Grid, Central Hudson, Rochester Gas & Electric, and all of the municipal pocos all require this ground rod grounding electrode conductor to be #4 cu. Their connection with the Public Utilities Authority permits them to surpass the NEC.
Brad Baxter said:OK so in other words what your saying is no matter what the NEC says that you cannot use #6 and have to use a #4 to both ground rods regardless?.....
Brad Baxter said:....Why have a NEC then? or are they going to give you a NEC part 2 upgraded book for what they want?
Brad Baxter said:Can someone show where it says in the NEC that you can use a #6 bare copper ground wire to both ground rods. There is a argument that you must use a #4 bare copper minimum to both ground rods for a 200 amp service.
electricmanscott said:You'd think those that require #4 would know what a waste of wire that requirement is.
C3PO said:Look at Section 250.66(A)
NEC still only requires #6 for rods, even then.tyha said:the building was wood framed and incomming water was plastic.
tyha said:we just did a church that had a 200 and a 400 disconnect feeding 2 panels on the inside. the plans called for a 2/0 to building steel and a 2/0 to water pipe and a #6 to ground rod. the building was wood framed and incomming water was plastic. we placed 2 ground rods (1 at each disconnect) run a 2/0 to each disconnect from the ground rods and connected the ground rods together with 2/0 cadweld
buckofdurham said:Some juisdictions requirements are that if you use #4 it does not have to be physically protected. #6 would have to be sleeved (protected) down the wall.