Why is the ground wire in MC cable insulated? I feel like its more cost without anything in return so I'm guessing their must be a reason.
We talked about redesigning NM to have an insulated ground. :happyyes:
Uninsulated EGCs in boxes are a never ending problem, especially now with AFCI and GFCI breakers that readily show up the problem of an EGC contacting the neutral if someone is not very careful installing devices.
Also, unlike NM, MC is likely to be used at higher voltages in commercial installations, so a bare EGC floating around in device boxes is asking for trouble.
So, really, an insulated EGC in NM equals higher quality and a safer, more trouble free installation IMO.
-Hal
As far as MC-AP, as far as I'm concerned it should be considered type AC. MC was never allowed to use the armor as an EGC and unless the ground wire is required to be brought into the box and bonded to the box with a ground screw, I don't see the difference between it and AC. They both rely on just the box clamp to armor to provide the ground bond. I'm thinking the NEC caved to some manufacturer once again.
We talked about redesigning NM to have an insulated ground. :happyyes:
Uninsulated EGCs in boxes are a never ending problem, especially now with AFCI and GFCI breakers that readily show up the problem of an EGC contacting the neutral if someone is not very careful installing devices.
Also, unlike NM, MC is likely to be used at higher voltages in commercial installations, so a bare EGC floating around in device boxes is asking for trouble.
So, really, an insulated EGC in NM equals higher quality and a safer, more trouble free installation IMO.
As far as MC-AP, as far as I'm concerned it should be considered type AC. MC was never allowed to use the armor as an EGC and unless the ground wire is required to be brought into the box and bonded to the box with a ground screw, I don't see the difference between it and AC. They both rely on just the box clamp to armor to provide the ground bond. I'm thinking the NEC caved to some manufacturer once again.
-Hal
Missed it. Is there a thread?
JMHO, it all comes down to a fault path>
~RJ~
How's this for a guess, the cable was originally designed for pools where an insulated EGC was required and MC was easier to run than a metallic raceway. Of course this has changed.
Thomas Horne said:[FONT=Verdana, Arial][FONT=Verdana, Arial]The restrictions on wiring methods are based on the fire history of that type of occupancy. Since the jacket of type AC cable is the Equipment Grounding Conductor (EGC) if the jacket is damaged the EGC will be broken. In type MC cable any damage that will break the separately insulated EGC is likely to break the other circuit conductors and fault out the circuit. So in places were physical damage to the cable is more likely, such as a commercial garage or movie studio AC is forbidden. In places were large numbers of people are at risk such as movie theaters it is also forbidden. [/FONT][/FONT]
Looking for the history of when and why MC came about, I found this. From the Mike Holt archives, a post by Thomas Horne dated Feb. 25, 2002:
So here we have yet another opinion that MC came about because a separate insulated EGC offers a more reliable ground conductor.
-Hal