John Billig
Member
- Location
- Wellington, Colorado
I posted a question previously on bonding and grounding and the responses I received has brought up another question I have. My current home will have a 200 amp panel with a 200amp main breaker. The grounding electrode will be connected from the footing rebar to the ground bus in the panel. The neutral bus and ground bus in the panel will not be joined at the house panel. I have a meter/breaker enclosure back at the transformer which is 300 feet away. I was instructed to run 4 wires from the 200amp meter/breaker enclosure to my house panel and join the ground wire and neutral together at the meter/breaker enclosure. My question is why do I need the ground wire in the feeder conduit? Wouldn't it make more sense to drive a ground rod at the meter/breaker enclosure and attach to the neutral/ground lug? Would save on running a ground wire the 300+ feet.