You only need one EGC and as far as the 6" rule, this may be more applicable.
300.14 Length of Free Conductors at Outlets, Junctions,
and Switch Points. At least 150 mm (6 in.) of free
conductor, measured from the point in the box where it
emerges from its raceway or cable sheath, shall be left at each
outlet, junction, and switch point for splices or the connection
of luminaires or devices. Where the opening to an outlet, junction,
or switch point is less than 200 mm (8 in.) in any dimension,
each conductor shall be long enough to extend at least
75 mm (3 in.) outside the opening.
Exception: Conductors that are not spliced or terminated
at the outlet, junction, or switch point shall not be required
to comply with 300.14.