Re: Ground wire passing Thru Boxes unbroken
This section does not relax the requirement of grounding (bonding) a metallic box when used with a non-metallic raceway method.
If the box is grounded (bonded) by some other means such as a metallic raceway, then yes, the EGC not spliced can be pulled through without terminating to that box. However, section 250.80 and 250.86 require the box the be grounded by some means. The most practical way to do so is by attachment of the egc pulled through the box.