Does the ground wire in a circuit need to have physical protection (e.g. romex) as do hot and neutral, or can it be just floating without protection?

[ December 23, 2003, 03:06 PM: Message edited by: wiredanny ]
 

earlydean

Senior Member
Re: Ground Wire Protection

250.120 requires the EGCs smaller than #6 to be protected by raceway or armor, etc.
 