Hello all!
I inherited an interesting job and would like some feedback.
Currently, I have a customer-owned pole with a 200-amp meter main/service entrance that is feeding a 200-amp subpanel in a detached steel garage. The garage is about 10 feet away of the pole. The garage subpanel is feeding a mobile home with a 200-amp main-breaker load center about 60 feet away.
The pole, the garage, and the mobile all have their own grounding rods. And all the runs are underground in SCH 40 PVC and this is all new construction, all done by others.
The run between the garage and mobile is unfinished at the garage. It is just stubbed outside the garage directly behind the garage subpanel on the inside. The builder already pulled the wire and used three, 3/0 copper. They want me to finish the job and hook up to the sub in the garage thus feeding power to the mobile.
I usually use a direct-burial mobile-home-feeder cable that includes the ground for this type of job. My question is, do I need to add a ground wire to their 3-wire run? Thank you!
I inherited an interesting job and would like some feedback.
Currently, I have a customer-owned pole with a 200-amp meter main/service entrance that is feeding a 200-amp subpanel in a detached steel garage. The garage is about 10 feet away of the pole. The garage subpanel is feeding a mobile home with a 200-amp main-breaker load center about 60 feet away.
The pole, the garage, and the mobile all have their own grounding rods. And all the runs are underground in SCH 40 PVC and this is all new construction, all done by others.
The run between the garage and mobile is unfinished at the garage. It is just stubbed outside the garage directly behind the garage subpanel on the inside. The builder already pulled the wire and used three, 3/0 copper. They want me to finish the job and hook up to the sub in the garage thus feeding power to the mobile.
I usually use a direct-burial mobile-home-feeder cable that includes the ground for this type of job. My question is, do I need to add a ground wire to their 3-wire run? Thank you!