Where in the code does it specify that we must have a ground wire between the disconnect and the panel and what determines this? Thank you!!!
 
ALLELECTRIC95 said:
Where in the code does it specify that we must have a ground wire between the disconnect and the panel and what determines this? Thank you!!!


NEC Article 250?

Can you be a little more specific.

steve
 
I orginally asked.... Where does it address the requirement for a ground wire between the service disconnect (located on building) and the panel (located inside building) in the NEC?

And I was instructed to see 250.122.

Now I am being asked where it spells out what determines this requirement and why.

Hope that helps.
 
ALLELECTRIC95 said:
. . . Now I am being asked where it spells out what determines this requirement and why. . .
250.122 just spells out how to size the grounding conductor. You need to study all of Part VI in Article 250 (250.110 through 250.126). You know, I would also recommend that you purchase a copy of the 2008 Edition of the NFPA NEC Handbook. :)
 
ALLELECTRIC95 said:
I orginally asked.... Where does it address the requirement for a ground wire between the service disconnect (located on building) and the panel (located inside building) in the NEC?

And I was instructed to see 250.122.

Now I am being asked where it spells out what determines this requirement and why.

Hope that helps.

Try 215.6 and 250.134(A)
 