I have ran into a few older homes that have sub-panels that are fed without an equipment grounding conductor. So the grounded/neutral conductor and equipment grounds from the branch circuits are landed together. I have always learned that the nuetral/grounded conductor and equipment ground should only be bonded at the main service disconnect. I was wondering if anybody could explain what would happen if there was a ground fault in one of the branch circuits? Would the current travel back to the main panel through the neutral, thus violating code that the nuetral should never carry fault current? So, I am wondering if I should run an equipment ground back from the sub-panel to the main panel??
I have also run into systems that are similar to this except there is a grounding electrode at the sub-panel which all the equipment grounds are tied to. Is this okay?
Thanks for your help.
I have ran into a few older homes that have sub-panels that are fed without an equipment grounding conductor. So the grounded/neutral conductor and equipment grounds from the branch circuits are landed together. I have always learned that the nuetral/grounded conductor and equipment ground should only be bonded at the main service disconnect. I was wondering if anybody could explain what would happen if there was a ground fault in one of the branch circuits? Would the current travel back to the main panel through the neutral, thus violating code that the nuetral should never carry fault current? So, I am wondering if I should run an equipment ground back from the sub-panel to the main panel??
I have also run into systems that are similar to this except there is a grounding electrode at the sub-panel which all the equipment grounds are tied to. Is this okay?
Thanks for your help.