Should not, if your loadcenter has the required bonding jumper. In this case all you are doing is bonding the service raceway and that can be accomplished on either end. You are not depending on the conduit for the fault path as the meter and loadcenter are bonded to the neutral.
Should not, if your loadcenter has the required bonding jumper. In this case all you are doing is bonding the service raceway and that can be accomplished on either end. You are not depending on the conduit for the fault path as the meter and loadcenter are bonded to the neutral.
I havnt done much resi , But I thought you only have to bond nuetral to ground at main disco only not at the meter ?
Should not, if your loadcenter has the required bonding jumper. In this case all you are doing is bonding the service raceway and that can be accomplished on either end. You are not depending on the conduit for the fault path as the meter and loadcenter are bonded to the neutral.
Not necessarily.For my own info, the only place you are required to bond at both ends is the a GEC as per 250.64(E) correct>