m73214 said:
IMO, the fact that you are doing this takes the KO situation out of the equasion. Ask the AHJ to refer you to an article that backs up his position.
If he's using a metallic raceway I don't believe that to be true. According to Michael Johnston of the IAEI if you are using a metallic raceway the wire type EGC that you install is really secondary protection.
He explained that because of skin effect under a ground fault current a majority of the fault current will travel on the conduit rather that on the wire type EGC. Because of this it is important to always ensure bonding around concentric knockouts.
Now I know the NEC only requires this for circuits over 250v to ground. But I think if the AHJ wants the bushings than you put them in. After all he has the final say. You can cry a river, call his boss and complain all you want. It still won't stop him from holding up your approval until he get's what he wants.
Also, as we all know there are two types of concentric knockouts. Those that when you try to knockout the 1/2" opening the entire knockout falls out. And those that are impossible to knockout and you need to drill the opening out.
Call me stupid, but am I the only one who's ever been told about the skin effect issue in regards to ground faults? If you've heard of it, let me know, I'd hate to think I was wrong all these years but it does make sense to me.
Basically if you install a wire type EGC in a metal raceway. Both are required to be bonded which basically makes them the same conductor. Except that one is inside the other. Skin effect is the tendency for electrons to travel on the surface of a conductor. Since the metal raceway is the outermost surface it makes sense to me that more current would be on the raceway than the conductor.
Again, call me stupid but it makes sense to me.