Wher in the NEC can i find the conditions or prohibited use of a grounded conductor used as a current carrying conductor?
Any help will be appreciated.
 
Re: Grounded conductor as current carrying conductor

Do you mean "grounded," as in what is commonly called "neutral"? If so, then that conductor carries current all the time.

Do you mean "grounding," or more properly "equipment grounding conductor," or what is commonly called "ground (green or bare copper) wire"? If so, look at 250.6 and 250.24(A)(5). I am sure there are other, and perhaps more relevant, code articles. But I have to run to a meeting, and can't look them up now.
 
Re: Grounded conductor as current carrying conductor

In most situations the "Grounded Conductor" is a current carrying conductor. It is not prohibited.

Are you thinking about the "Equipment Grounding Conductor"?

Roger
 
Re: Grounded conductor as current carrying conductor

If you are talking about an installation where you have and existing conductor in conduit that was a ground and now you would like use as a hot? You should be allowed to do this as long as you mark appropriately on the conductor that it is no longer a ground (lots of marking tape). I know I'm going to get flamed for this, its not the best senario but sometimes its acceptable.
Also, if you are going to use the conduit as the equipment grounding conductor, then make sure all the connections have been properly made including bonding jumpers, incase the previous installer decided because there used to be an equipment ground, he didn't have to do a good job grounding the conduit.