Grounded conductor being broken

leatham

Member
Location
California
Occupation
ECH
While I was reading on the 25 tap rule I noticed in 2023 handbook exhibit 240.7 it shows the secondary side of the transformer breaking the grounded conductor is this legal?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If it's being switched with the ungrounded conductors there's no problem
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I don't see how that shows a breaker in the grounded conductor. It is a single line diagram so it's quite schematic. It assumes you would know that where it shows the secondary being grounded you are only grounding the neutral and that where it shows a breaker it would only open the ungrounded conductors.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Jagged, it just a rather poor single line graphic which makes it confusing but not incorrect.
 