Grounded conductor in AC disconnect after inverter

Status
Not open for further replies.
No, unless the disconnect is a main with a line side tap from the service. Generally, the disconnect would be treated like a sub-panel. The AC grounded conductor and the grounding conductor should be isolated from each other.
 
No, unless the disconnect is a main with a line side tap from the service. Generally, the disconnect would be treated like a sub-panel. The AC grounded conductor and the grounding conductor should be isolated from each other.

In addition, the grounded conductor should not be switched in the AC disconnect for grid tied inverters.
 