We are working on a project design where we will be removing a control panel that incorporates the service disconnect and placing a regular knife switch service disconnect to allow additional changes to take place. The building is served by a 480V utility transformer with an underground utility secondary feed to the control panel. The original design plans called for 4-#3/0; which makes sense for a 200A service disconnect. However, when at the site we opened the control panel. The phase conductors are terminated at the service disconnect breaker but the expected grounded conductor is not there. Instead, there is a smaller sized conductor with green tape (ran with the phase conductors) landed under a lug labeled "equipment ground only". There does not appear to be a place to land the grounded conductor. There is a grounding electrode system present. We will be contacting the utility to open the transformer and see where smaller conductor is attached. It kind of looks to me like the grounded conductor is improperly identified and it has been downsized from the original drawings which looks like it may be allowed per 250.24.C.1. Anybody suspecting something otherwise or see this before?
Based on 250.24.C, I believe the grounded conductor must be ran and must be terminated at both ends. We will need to check the size and see if it is of adequate size even though it is not the same size as the phase conductors. We would like to see it changed out to the same size as the phases, but we are thinking the size may be allowed as it is.
Based on 250.24.C, I believe the grounded conductor must be ran and must be terminated at both ends. We will need to check the size and see if it is of adequate size even though it is not the same size as the phase conductors. We would like to see it changed out to the same size as the phases, but we are thinking the size may be allowed as it is.