I have a 1600A feeder leaving a switchboard, going thru an ATS, then back to the switchboard. The generator/ATS is NOT an SDS. The generator output breaker is 1200A. The conductors to (and back from) the ATS and switchboard are 6 sets of 500 AL, 2 sets in each pipe. The conductors from the gen to the ATS are 6 total sets of 350 AL, in 3 pipes. Max demand over 3 years is 380 amps. What size grounded conductors should I use?
My thoughts: Its temping to go real small, maybe minimum size. Under normal operation, the neutral to/from the ATS wont be carrying anything. Minimum size per 215.2(A)(2) is 350MCM AL, which would be a 2/0 in each pipe. Also was kinda thinking that (3) 2/0 exceeds the demand figure (assuming perfectly balanced), but not sure that makes any logical sense to compare those two that way. I guess I could say absurd worst case is the 136 KW all on one phase which would be like 1100A This is large facility, im not doing a neutral calc, it would take half a week.
My thoughts: Its temping to go real small, maybe minimum size. Under normal operation, the neutral to/from the ATS wont be carrying anything. Minimum size per 215.2(A)(2) is 350MCM AL, which would be a 2/0 in each pipe. Also was kinda thinking that (3) 2/0 exceeds the demand figure (assuming perfectly balanced), but not sure that makes any logical sense to compare those two that way. I guess I could say absurd worst case is the 136 KW all on one phase which would be like 1100A This is large facility, im not doing a neutral calc, it would take half a week.