250.24(C) requires that with a grounded service supply, the grounded conductor be routed to the switchgear along with the ungrounded conductors. 250.24(C)(2) states the size shall be based on the size of the phase conductors and, when run in parallel, based sum of the sum of the total circular mil, however, it goes on to say "Where installed in two or more raceways, the size of the grounded conductor in each raceway shall be based on the size of the ungrounded service-entrance conductor in the raceway but not smaller than 1/0 AWG" (underline added).
Lets take the scenario of two conduits feeding an 600 amp service with
500kmil runs in each. The sum is 1000 kcmil thus requiring a 2/0 by 250.66
BUT each conduit has 500's and the underlined section makes me think that since the parallel service is in two conduits that only a 1/0 is required based on the 500 kcmil in each conduit.
What is the required size ?
Lets take the scenario of two conduits feeding an 600 amp service with
500kmil runs in each. The sum is 1000 kcmil thus requiring a 2/0 by 250.66
BUT each conduit has 500's and the underlined section makes me think that since the parallel service is in two conduits that only a 1/0 is required based on the 500 kcmil in each conduit.
What is the required size ?