Ok, here is the skinny. I have come across a situation in a commercial setting where the grounded conductor has 2V to ground at its panel and in the field. The set up is this: 208V single phase/ 100A service fed with #3AWG THHN STR COPPER. The Panel is a IG panel that is fed this way: 208V from the XFMR to an 100A breaker at another panel, then from there it goes underground(50ft) to a disconnect#1, then to an UPS, then to disconnect#2, then back underground(50ft) to the IG panel. Now this is what I found, the IG from the IG panel should be unbroken to the XFMR but, the contractor spliced it at the panel where the IG panel is being fed from. Secondly, I found at disconnect#2: the grounded conductor is bonded. My thinking is the grounded conductor may need to be larger to handle the load. The load is high on the grounded conductor at 48A. The customer is having problems with their computers and the computer guys are telling me the problem is the 2V on the neutral. I hope you can sift thru this muck and find some gold!