Re: Grounded Conductor
For a multiwire branch circuit each grounded condcutor must terminate in an individual terminal in the panel, per UL standard 67 and now the 2002 NEC. Ask your self what happens when the grounded conductor on a multiwire branch circuit is opened to the loads....
Also I don't see the savings on this, you have to go to the truck and get a roll of 8 AWG instead of using 12 AWG as a home run.