Junior plan reviewer
I have fire pump fed from POCO transformer 208V, three phase, FLA 143A and service phase conductos of 3#3/0. Grounded conductor has to be brought to service equipment. Question is the size of the grounded conductor. Would 250.24(C)(1) or 250.24(C)(3) apply?
 
I have fire pump fed from POCO transformer 208V, three phase, FLA 143A and service phase conductos of 3#3/0. Grounded conductor has to be brought to service equipment. Question is the size of the grounded conductor. Would 250.24(C)(1) or 250.24(C)(3) apply?

250.24(C)(1)
 
250.24(C)(3) is for a Delta service. A 480 volt fire pump can be fed from a Wye service.
 