Hello All,
I have a 13.8 Delta to a 480V Y transformer feeding 480V street lighting. I have connected the XO to the grounding grid system that is permissible to use to ground the system, there is a factory bonding strap from the XO to transformer. I also have attached at the transformer EGC. I pulled all ungrounded circuit conductors plus the EGC to a 480V panel and attached the EGC to the grounding bar. All lighting is 480V. I have no line to Neutral loads. The Inspector said I still need to pull a Neutral conductor.
Whats up with that?
I have a 13.8 Delta to a 480V Y transformer feeding 480V street lighting. I have connected the XO to the grounding grid system that is permissible to use to ground the system, there is a factory bonding strap from the XO to transformer. I also have attached at the transformer EGC. I pulled all ungrounded circuit conductors plus the EGC to a 480V panel and attached the EGC to the grounding bar. All lighting is 480V. I have no line to Neutral loads. The Inspector said I still need to pull a Neutral conductor.