Not if the neutral will not be needed by any loads.Am I required to use a neutral conductor in a 3ph wye (120/208) feeder that will be used to feed a bank of airconditioning units? - no other loads will be used from this sub-panel. grateful if you could comment on this.
Why ask why?Why was the other duplicate post (located in NEC section) deleted when this is an NEC rule issue and not an engineering/design issue?
Good a reason as any.Just curious
True. However:How about the need of a 120 volt receptacle for servicing? Then you would want the neutral.
So, it's presumed that any required receptacle will be supplied elsewhere.... no other loads will be used from this sub-panel.
Just curious
Thanks
If you do that, the subpanel, and breakers cannot be slash rated.
Some breakers are rated 120/240v, and some 240v. The former relates to line-ground voltage, and the latter to line-line voltage.What do you mean by slash rated