Probably not as complicated as I think it is but I could use some help with this.
Customer will have a 400a single phase 120/240v generator a few hundred feet from the house.
Inspector wants a separate grounding means at generator.
Transfer switch is inside the house so there will be 2qty additional generator feed 200a breaker disconnects at the house.
Utility feed to the transfer switch will have 2qty 200a breaker disconnects bonded and grounded outside of the house to the ground rods.
Transfer switch will NOT have neutral and ground bonded since it will not be 1st means of disconnect for utility feed.
*Are the ground and neutral to be bonded at the generator to make a separately derived system requiring a switched neutral in the transfer switch?
*Is it ok when the house is connected to house ground rods & generator ground rods 200ft away?
*I would assume I still run a ground wire from the generator to the transfer switch which now connects both sets of ground rods...?
*Is the ground from the generator to the transfer switch to be grounded and bonded again at the disconnects right outside of the house and to the house ground rods before it goes into the house or are the disconnects at the generator considered the first means of disconnect?
Thank you for the help!
Customer will have a 400a single phase 120/240v generator a few hundred feet from the house.
Inspector wants a separate grounding means at generator.
Transfer switch is inside the house so there will be 2qty additional generator feed 200a breaker disconnects at the house.
Utility feed to the transfer switch will have 2qty 200a breaker disconnects bonded and grounded outside of the house to the ground rods.
Transfer switch will NOT have neutral and ground bonded since it will not be 1st means of disconnect for utility feed.
*Are the ground and neutral to be bonded at the generator to make a separately derived system requiring a switched neutral in the transfer switch?
*Is it ok when the house is connected to house ground rods & generator ground rods 200ft away?
*I would assume I still run a ground wire from the generator to the transfer switch which now connects both sets of ground rods...?
*Is the ground from the generator to the transfer switch to be grounded and bonded again at the disconnects right outside of the house and to the house ground rods before it goes into the house or are the disconnects at the generator considered the first means of disconnect?
Thank you for the help!