I'm working on a system fed by a single phase 120/208VAC source. L1 and L2 are #2 from the plug to the main breaker. Ground is #6 and N is #10.
There are two power supplies and a PLC connected between L1 and N. There are no other line to neutral loads. The components are protected by 5A fuses. The circuit current is about 4A. #10 was used because it's the smallest wire the plug can handle.
The inspector says the neutral is grounded and needs to be #8 based on the NFPA 70-2023 Table 250.102(C)(1).
Yes, the neutral is bonded to ground inside the feeder panel. Are there are any other codes that would apply?
There are two power supplies and a PLC connected between L1 and N. There are no other line to neutral loads. The components are protected by 5A fuses. The circuit current is about 4A. #10 was used because it's the smallest wire the plug can handle.
The inspector says the neutral is grounded and needs to be #8 based on the NFPA 70-2023 Table 250.102(C)(1).
Yes, the neutral is bonded to ground inside the feeder panel. Are there are any other codes that would apply?