Grounded or Ungrounded 240 Delta for Power
bcoontz
New member
Ohio
Good Morning!
We "currently" have an Ungrounded 240V Delta for supplying equipment that can't use 480V
We have the option, in our new plant of having the 3 phase 240V Power Panels wired either Ungrounded Delta or Corner Grounded Delta.
Any Pro's or Con's on either system?
Thanks!
Bob
Re: Grounded or Ungrounded 240 Delta for Power
I guess it depends on whether you want a grounded power system or not. Personally, if I was going grounded I would want a wye ocnfiguration, but that is just a personal preference because I rarely if ever see corner grounded anything.
The primary reason for an ungrounded system is if your plant cannot tolerate a ground fault very well. If you can live with a ground fault tripping your power, than go grounded. If not, then go ungrounded. Its as simple as that.
If it is in fact, a totally new plant, then wouldn't the first choice be 480/277 wye with xfmrs to derive 208/120 wye.
Then use xfmrs to derive any "special" voltages that are needed such as 240.
Generally for 3-phase 240V., I would prefer a system with a grounded conductor (whether the grounded conductor actually serves load or not).
Ungrounded distribution systems require a highly degree of troubleshooting experience. Many electricans are not trained on finding ground faults in ungrounded systems.
Corner grounded systems require non-standard distribution equipment (i.e. Square D QO2xxH breakers not QO2xx style).
At least one industrial in this area is now buying transformers with 240Y/138 secondaries. This is a standard rating for drive isolation designs. This arrangement gives them the advantages of 240V not 208V line to line and a center grounded distribution. They only feed 3 phase loads from these panels.
edit: fixed part number of breakers
[ September 28, 2005, 12:36 PM: Message edited by: jim dungar ]