grounded PV conductors

Status
Not open for further replies.

naprstek

New member
Location
New York
I was taught that the PV grounded conductor should continuous from the array to the inverter.
as per NEC 2011 690.41

anding NEC Requirements for Solar Photovoltaic Systems"
shows the grounded conductor wired through a Square D disconnect at 1:20:37

?????
 
In Mike Holt's book, he shows a picture of the inside of a dc disconnect that meets the Exceptions to 690.13. You can break the grounded conductor if the disco is: (1) used for PV array maintenance only; (2) accessible to qualified persons only; and, (3) rated for the max possible voltage and current.

Maybe that's what you're looking at? Hard saying without more info.
 