Hello,
We have a standard 208/120V commercial service from a utility pad mount transformer. The transformer has the neutral and ground bond via a nice copper strap. We will carry three phase conductors to our main service panel. The question came up about the neutral & ground conductors.
We have a standard 208/120V commercial service from a utility pad mount transformer. The transformer has the neutral and ground bond via a nice copper strap. We will carry three phase conductors to our main service panel. The question came up about the neutral & ground conductors.
- I believe we only need a neutral since it will be bonded on both ends to ground. It can be sized smaller than the phase conductors by table 250.102(C)(1)(NEC 2017). Intuitively this makes sense to me since it is just carrying any imbalance in the loads.
- Others want to run a fullsize neutral and a separate ground conductor. This seems wrong since the neutral is bonded on both ends. If anything this creates parallel paths for the neutral or ground current.