Grounded Switches.
michael nye
California
Where in the code does it break down the method of grounding switches, when did it change and become code I've looked, but cannot find. Thankyou for any help
luke warmwater
Re: Grounded Switches.
1999 NEC 380-9(b)
The oldest book I have in front of me is 1993. I believe this is when it changed. 380-12...Metal face plates for snap switches shall be effectively grounded where used with a wiring method that includes or provides an equipment ground.
michael nye
California
Found it with the 380-12 but does this mean if it's a commercial application and the metal box is grounded then the switches do not need tailed as in an residential situation, thank's guy's.
tom baker
Bremerton, Washington
Master Electrician
Michael-
Switches in a metal box do not need "tails" IE equipment grounding jumpers. The switch is not part of the ground fault current return path as a recptacle is, they need the tail or have to be self grounding.
mikeackley
Washington
Michael Nye:
Just FYI, if you found switch grounding provisions in in 380-12, that tells me you are using 1999 NEC. So that explains why your code book skips from 402-12 to 410 - because that's what 1999 NEC does.