I found an outdoor sub panel today that I believe one of our guys did wrong and I, er, "fixed" it. He happened to drive up at the end of the day and "caught" me working in "his" panel and claimed I was wrong. He drove off in a fit. I don't know which code articles to cite. So I come to the professionals for guidance! 
There is a 480v feed coming out to a parking lot light pole- besides the regular wires that feed the light I've got two high voltage hots, and the rigid ground from the panel inside the building. This 'additional' feed goes into a little 40 amp 3r transformer (480 -> 120/240) mounted on a nice unistrut frame back to back from a 3r panel that serves some 120v lighting loads outside. There's a ground rod at this panel. [PS The clamp was above ground. Where's the code for that? I'm going to bust some rock and drive it under on Monday.]
First of all, I think the transformer should have a neutral from H2 and H3 back to the building panel. This is your typical H1 H2 H3 H4 transformer where 480 is applied to H1 and H4 and H2 and H3 are tied together in the middle. But I didn't say that because I wasn't sure. The diagram wasn't clear...
Next, the X2 and X3 (low voltage side) are correctly connected together in the transformer to the neutral bar in the panel (X1 to X4 is 240v and feeds the lugs) but he bonded the neutral in the panel to ground. Again, there's already a ground path from the panel to the local rod via some bare copper and it's grounded to the rest of the system via the rigid conduit. (344.60) I say no bonding here because this isn't a service disconnect or a service entrance panel. And now he's got a parallel ground path to boot.
I know, probably asked and answered a dozen times on this forum, but I've only read posts to page 52 or so and I'm not good with the search results.
I eagerly await your future reply!
Jeremy
Tulsa, Ok
There is a 480v feed coming out to a parking lot light pole- besides the regular wires that feed the light I've got two high voltage hots, and the rigid ground from the panel inside the building. This 'additional' feed goes into a little 40 amp 3r transformer (480 -> 120/240) mounted on a nice unistrut frame back to back from a 3r panel that serves some 120v lighting loads outside. There's a ground rod at this panel. [PS The clamp was above ground. Where's the code for that? I'm going to bust some rock and drive it under on Monday.]
First of all, I think the transformer should have a neutral from H2 and H3 back to the building panel. This is your typical H1 H2 H3 H4 transformer where 480 is applied to H1 and H4 and H2 and H3 are tied together in the middle. But I didn't say that because I wasn't sure. The diagram wasn't clear...
Next, the X2 and X3 (low voltage side) are correctly connected together in the transformer to the neutral bar in the panel (X1 to X4 is 240v and feeds the lugs) but he bonded the neutral in the panel to ground. Again, there's already a ground path from the panel to the local rod via some bare copper and it's grounded to the rest of the system via the rigid conduit. (344.60) I say no bonding here because this isn't a service disconnect or a service entrance panel. And now he's got a parallel ground path to boot.
I know, probably asked and answered a dozen times on this forum, but I've only read posts to page 52 or so and I'm not good with the search results.
I eagerly await your future reply!
Jeremy
Tulsa, Ok