Grounded vs. Nuetral
ryan_618
It was posted at this forum (by a vey knowledged individual) that in a 208y/120 system that "the grounded conductor is always a current carrying conductor". Can that individual please teach an ill-informed inspector like me please?
If this is the case, shouldn't every multi-wire branch circuit containing three phases + grounded be derated as more than three current carrying conductors?
Re: Grounded vs. Nuetral
Hi Ryan, It is my understanding that when you only use 2 phase conductors with one neutral from a 208Y/120 system that they will all be current carrying conductors, because the two phases in use are not 180 degrees apart.
They would be 120 and 240 degrees apart alternately so they do not balance out.
Use all 3 phase conductors and all is well.
Here is a reference for you.
310.15(B)(4)(b) In a 3-wire circuit consisting of two phase wires and the neutral of a 4-wire, 3-phase, wye-connected system, a common conductor carries approximately the same current as the line-to-neutral load currents of the other conductors and shall be counted when applying the provisions of 310.15(B)(2)(a).
Ryan, it is very rare that all phases would be equal at their respective times making the grounded conductor neutral in the zero sense.
But, the unbalanced current on this conductor would only add heat in proportion to it's loading and could never add say another total 20 amps to (3) 20 amp phases, and as you know, would come closer to zero as the other phases increased towards 20 amps. (LINEAR loads no HARMONICS in this conversation please ;) )
The most the grounded conductor could see would be 20 amps if only one phase were loaded and the other two were off.
Wye neutral load calculation
SQ root of
I^2A +I^2B +I^2C -(IAxIB)-(IBxIC)-(ICxIA)
Roger
[ October 01, 2003, 07:48 PM: Message edited by: roger ]
Ryan
A neutral conductor is considered a current carrying conductor.
310.15(B)(4) permits a neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted in the ampacity adjustment.
Pierre
But we're glad you're back.
Roger
Ryan,
I misstated my answer in the other thread and have clarified it in that thread. Bob's first post in this thread said what I should have said in the other thead.
Don