Grounded wire

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
All power co poles have a grounder wire ran with their hot wire or hot wires , is their any case were this grounded wire does not connect to the grounded or neutral wire on the secondary side, service wires grounded or neutral ?
 
In general no. They bond primary and secondary grounded conductors together whenever they coexist at same structure.

Ungrounded secondary systems are probably rarely found when it comes to utility fed service. Most users of ungrounded systems are separately deriving them AFAIK within their own facility.
 
Grounded

Grounded

If that is so where does the primary get the ground from?
 
If that is so where does the primary get the ground from?
If one conductor of both systems is bonded together then running a single conductor serves both systems. The conductor will not care which system it is connected to, it carries current from both systems, and you could connect it to hundreds of systems - which we do on POCO distribution systems. Every transformer is a separately derived system and every one of them bonds to the MGN of the primary system - ungrounded systems would be the exception if there even is any supplied by any POCO's, those are usually derived by customer transformers and not the POCO.
 
Ground wire

Ground wire

To make simple the ground rod at my home is connected to a ground rod at a pole a mile down the road?
 
Ground wire

Ground wire

Do most poco use a Y secondary at there sub stations?
 
Do most poco use a Y secondary at there sub stations?
I think there are some delta distribution systems out there but most of them are Y, and most use the neutral for most transformers connected to the system. If they don't use the grounded neutral then they need a two bushing transformer instead of a single bushing - more expense. Of course a three phase pad mount won't really be much different as it will use three bushings either way.
 