If that is so where does the primary get the ground from?
If one conductor of both systems is bonded together then running a single conductor serves both systems. The conductor will not care which system it is connected to, it carries current from both systems, and you could connect it to hundreds of systems - which we do on POCO distribution systems. Every transformer is a separately derived system and every one of them bonds to the MGN of the primary system - ungrounded systems would be the exception if there even is any supplied by any POCO's, those are usually derived by customer transformers and not the POCO.If that is so where does the primary get the ground from?
Through the combination of primary and secondary neutrals and their common connections to the same ground electrodes, yes, IMHO.To make simple the ground rod at my home is connected to a ground rod at a pole a mile down the road?
Probably not that far away...the NESC code requires a grounding connection 4 times a mile for the utility system.To make simple the ground rod at my home is connected to a ground rod at a pole a mile down the road?
I think that domnic's concern is whether there is a metallic connection all the way to the mile-distant pole, not whether there are closer ground electrodes.Probably not that far away...the NESC code requires a grounding connection 4 times a mile for the utility system.
I think there are some delta distribution systems out there but most of them are Y, and most use the neutral for most transformers connected to the system. If they don't use the grounded neutral then they need a two bushing transformer instead of a single bushing - more expense. Of course a three phase pad mount won't really be much different as it will use three bushings either way.Do most poco use a Y secondary at there sub stations?