Re: groundig a concession trailer
If you are supplying the trailer/concession from the generator via a cord and plug situation, no you do not need to ground the trailer or the generator.
If you supply them from the generator with a hard wired situation, then yes you need to use ground rods.
"250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be grounded and shall be permitted to serve as the grounding electrode for a system supplied by the generator under the following conditions:
(1) The generator supplies only equipment mounted on the generator, cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and
(2) The non?current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are bonded to the generator frame."
I should add this as well:
"525.21 Rides, Tents and Concessions.
(A) Disconnecting Means. Each ride and concession shall be provided with a fused disconnect switch or circuit breaker located within sight and within 1.8 m (6 ft) of the operator?s station. The disconnecting means shall be readily
accessible to the operator, including when the ride is in operation. Where accessible to unqualified persons, the enclosure for the switch or circuit breaker shall be of the lockable type. A shunt trip device that opens the fused
disconnect or circuit breaker when a switch located in the ride operator?s console is closed shall be a permissible method of opening the circuit."