CSST Bonding Follow-Up
Since there appears to be continued confusion on
bonding of gas piping, specifically Corrugated, Stainless-
Steel Tubing (CSST), this article expands upon the Winter
2007 Construction Code Communicator article, ?CSST
Bonding ? What is Required?? and Section 250.104(B),
Other Metal Piping, of the 2005 National Electrical Code
(NEC/2005).
Section G2411.1 of the 2006 International
Residential Code (IRC/2006), Gas Pipe Bonding, which
applies to Group R-5 occupancies, and Section 310.1 of
the 2006 International Fuel Gas Code (IFGC/2006), Gas
Pipe Bonding, which applies to all occupancies other than
Group R-5, state the following:
Each above-ground portion of a gas piping system
that is likely to become energized shall be electrically
continuous and bonded to an effective ground-fault
current path. Gas piping shall be considered to be
bonded when it is connected to appliances that are
connected to the equipment grounding conductor
of the circuit supplying that appliance.
Referenced model codes supersede the
manufacturer?s recommendations. Therefore, contrary to
some manufacturers? installation recommendations, the
above sections prevail. No additional bonding is required
where there is electrical connection to any gas appliance;
the grounding conductor serves as the bonding means of
a gas piping system. If the installation meets the
manufacturer?s recommendations for bonding, this would
be considered above code requirements and acceptable.