Well I got Mike's grounding and bonding newsletter and it did just what it was supposed to do. Got me scratching my head.
Here's the one that got me.
Ground rods are not required at a separate building supplied by a 60 ampere 4 wire feeder (120/240 V -, 2 hots, neutral and ground, with the neutral floated at the separate building disconnect).
True or False.....Well it's false
I put ground rods at each building and bond them to the grounding bar in the panel at each out building. Just for the lighning to have a good path to ground and save some equipment hopefully.
Not to clear a ground fault.
May be I'm not saying this correctly.
Be gentle....Mike
Here's the one that got me.
Ground rods are not required at a separate building supplied by a 60 ampere 4 wire feeder (120/240 V -, 2 hots, neutral and ground, with the neutral floated at the separate building disconnect).
True or False.....Well it's false
I put ground rods at each building and bond them to the grounding bar in the panel at each out building. Just for the lighning to have a good path to ground and save some equipment hopefully.
Not to clear a ground fault.
May be I'm not saying this correctly.
Be gentle....Mike