I have been in ahj's that have made me bring GEC to cold water pipe and others that dont require it. Is this acceptable to not bring to water pipe?
tom baker said:A metallic water piping system is always:
Grounded per 250.52(A)(1) or
Bonded per 250.104
The bonding location only has to be accessible.
The grounding location has to be within 5 ft of the water pipe entrance into the building