We have an existing street lighting circuit that is fed by a 2400V/480V single-phase transformer. One phase is grounded. The circuit goes to the poles in direct-buried cable with no Equipment Grounding Conductor (The ld ways are not always the best ways!) Incorrect, I know, but that is how it is.
The circuit is to be refed from the other end due to a new building being built.
I am wondering if this system is required to be grounded.
250.20B requires the following systems to be grounded:
(1) if you can limit voltage-to-ground to 150V NO in this case (480V to ground)
(2) if it is 3p/4w Y NO in this case
(3) if it is 3p/4w D NO in this case
Question #1: Am I correct to say it doesn't need to be grounded?
Question #2: Would they be better off if the circuit to the poles was from an ungrounded system, since it would seem that it eliminates the danger of the pole becoming energized and shocking someone, since the system would have virtually no potential to ground?
Question #3: Any other idea on how to fix this, without digging it all up and installing an EGC?
Thanks for the help
The circuit is to be refed from the other end due to a new building being built.
I am wondering if this system is required to be grounded.
250.20B requires the following systems to be grounded:
(1) if you can limit voltage-to-ground to 150V NO in this case (480V to ground)
(2) if it is 3p/4w Y NO in this case
(3) if it is 3p/4w D NO in this case
Question #1: Am I correct to say it doesn't need to be grounded?
Question #2: Would they be better off if the circuit to the poles was from an ungrounded system, since it would seem that it eliminates the danger of the pole becoming energized and shocking someone, since the system would have virtually no potential to ground?
Question #3: Any other idea on how to fix this, without digging it all up and installing an EGC?
Thanks for the help