If the utility requires a ground in the meter can to the neutral bar, isn't that the same as bonding the neutral. If so, would that be per code to bond the neutrals again in service disconnect.
What do you mean by a ground in the meter? The meter base grounded conductor is bonded to the can but you would not run a separate egc to the service disconnect.
The utility company requires a grounding conductor from Neutral bar in meter can to ground rod.
Using the grounded conductor for grounding and bonding ahead of the service disconnecting means is acceptable from an NEC standpoint.
Chris
So you will still have to bond the neutrals again at the service disconnect. and that is per code
Can this ground be run in same conduit that feeds the service disconnect and be terminated in the gutter with rest of grounds on a ground bar
How would run the gec from the meter can to where?
So you are saying that if you bond the neutral in the service disconnect(Main bonding Jumper) , you do not have to run another GEC to the meter can.
So if I run a GEC to the neutral in the service disconnect and install main bonding jumper there, that you do not have to run a seperate GEC to meter can