Re: grounding a 400 amp service
Wayne, If you read 250.50 you will notice the first sentence says "If availible on the premises at each building or structure served, each item in 250.52(A)(1) through (A)(6) shall be bonded together to form a grounding electrode system".
As you know the six electrodes are metal underground water pipe, structural steel, ufer, ground ring, rod & pipe, or plates. If you you are the electrical contractor wiring the house and find no electrodes availible, you really only have three choices which are to add either a ground ring, plate, or rods. All electricians I know choose the easy way out unless otherwise specified. RODS.
The only thing I can add is even if the water service is not metalic you are still required to bond the copper water pipe used in the building.