TommyDRC
Member
- Location
- Louisville, KY USA
Hi all,
I usually wire motor control circuits and only work with small industrial control transformers. I'm now out of my element because I'm trying to wire a Buck-Boost transformer to be used as a general purpose transformer. More specifically, I'm having trouble figuring out how to ground this transformer. The transformer is a 1.5KVA BB transformer with a 240/480V primary and a 24/48V secondary. I'm using 2 three phase 230V legs on the primary side and tying X2 and X3 together on the secondary to generate 48V (I know that since I'm using two 3-phase 230V legs that I'm only getting 208V on the primary and about 40V on the secondary but that's okay). I'm then attaching two heating elements in parallel between X1 and X4. Per NEC 450.3(B) each element has a 2-pole secondary circuit breaker in series rated at 20A and the primary side has a 2-pole circuit breaker rated at 10A. Now that I've gotten that out of the way, here is my question...
Do I need to bond X4 to the case of the transformer and then bond the transformer case to my ground terminal strip in the cutoff enclosure? Also, how do I size these bonding wires? Do they need to be sized for the 50A that the primary circuit breaker would allow on the secondary side before clearing a ground fault? Thanks in advance for the help! I've read through NEC 250 and 450 several times plus multiple websites and feel thoroughly confused.
-Tommy
I usually wire motor control circuits and only work with small industrial control transformers. I'm now out of my element because I'm trying to wire a Buck-Boost transformer to be used as a general purpose transformer. More specifically, I'm having trouble figuring out how to ground this transformer. The transformer is a 1.5KVA BB transformer with a 240/480V primary and a 24/48V secondary. I'm using 2 three phase 230V legs on the primary side and tying X2 and X3 together on the secondary to generate 48V (I know that since I'm using two 3-phase 230V legs that I'm only getting 208V on the primary and about 40V on the secondary but that's okay). I'm then attaching two heating elements in parallel between X1 and X4. Per NEC 450.3(B) each element has a 2-pole secondary circuit breaker in series rated at 20A and the primary side has a 2-pole circuit breaker rated at 10A. Now that I've gotten that out of the way, here is my question...
Do I need to bond X4 to the case of the transformer and then bond the transformer case to my ground terminal strip in the cutoff enclosure? Also, how do I size these bonding wires? Do they need to be sized for the 50A that the primary circuit breaker would allow on the secondary side before clearing a ground fault? Thanks in advance for the help! I've read through NEC 250 and 450 several times plus multiple websites and feel thoroughly confused.
-Tommy