Re: Grounding a butane gas tank.
There are a couple points I would like to make.
1. A ground rod may be the worst of all choices for a grounding electrode. If it is in dry sand, it will not be of low enough impedance to do any good. 2. Two separate grounds may have a difference of potential between them. One is at a good earth ground and the other is not. 3. There should be no current on a grounding system. It is there to trip the overcurrent device and/or limit potential on the wiring if there is a fault. 4. OSHA requires all fuel storage vessels to be grounded. (OSHA CFR 1910.110).
Those butane tanks must be grounded to a good ground which should be to the plants ground electrode system which, if installed correctly, is bonded to the building steel. The column (if bonded) is an excellent ground for the tanks.
Butane will vaporize at 30 degrees at atmosphere pressure. Any leak and any spark will cause an explosion.
I work at a propane processing plant. There are no columns more than 40 ft from a ground rod (3/4 X 10). There is not an inch of conduit without a grounding conductor. Every motor has an additional external ground. Every section of cable tray is bonded. All external equipment grounds are 2/0 or larger even to the ground rods. The whole plant is Class 1 Division 2. We have over a million gallons of propane. I cannot over emphasize the importance of the grounding system.