On a generator installation there is no grounding conductor running from the generator to the transfer switch. It will be ground with a grounding electrode to the frame of the generator. Would you use table 250.122 or table 250.66 for this application? I would think that table 250.66 is the correct one. Also, 250.66(A) states that a grounding conductor that is sole connection to the grounding electrode shall not be required to be larger than 6 AWG cu or 4 AWG al. If the only purpose of this conductor is to connect the generator to a 5/8 x 8 CU ground rod would a #6 AWG cu conductor be sufficient? I am looking at the 2008 NEC Handbook - FYI.
Thanks!
Thanks!